Modification of the XLT coefficient in RFEM 6 (steel design)

Hi.

I noticed today that in the stability analysis for steel structures in RFEM 6 (6.14.0002), despite the checkbox for modifying XLT (Chi LT) by the factor F, the design does not change because the factor kc is always assumed to be 1.

I know that in EC 3 in RSTAB 8, based on the German NA and the literature, reductions were possible and were also taken into account there (depending on the moment distribution).

The question is how can I change or influence the factor kc in RFEM 6 from 1 to another value?

Best regards,
Natsu

Good day, I am very interested in how the XLT is involved in the stability analysis; this is a reduction factor that only enters the design when imperfections are taken into account.

Are you actually referring here to the steel design instead of the stability analysis?

A model or at least some images would be very helpful.

Best regards,

Nick

Hi.

What is meant is the steel design, or more precisely the substitute bar method. I simply used the wrong terms there. The following will include images related to what I actually meant.

It is important to mention that in RSTAB 8 and RFEM 6 it is the same model and I imported the model from RSTAB 8 into RFEM 6.

I will not refer to the latest EC3 in the following, as it was not clear to me whether the updated version has already been implemented in the programs or not. Therefore, the previous versions.

The following three images are excerpts from the standard, which give the indication that a reduction is possible due to the moment distribution. In the National Annex, reference is made to literature where further cases are treated beyond what is covered in the EC.
EC 3-1-1

EC 3-1-1 NA Germany


Below are my settings of the two programs. This concerns the same beam, same location, same support conditions, same internal forces. So everything is identical. The only difference in RFEM 6 compared to RSTAB 8 is the factor kc, which for whatever reason is set to 1.0, although the moment distribution is not rectangular.

RSTAB 8
grafik


RFEM 6



grafik

Hi Natsu,

Please make sure that in your model for the steel design the enumeration method is selected in the global settings.

If the envelope method is chosen, no exact calculation of k_c according to EN 1993-1-1 Table 6.6 is performed in RFEM 6. In this case, k_c is always assumed to be on the safe side with 1.0.

If you have any further questions or need support, I am happy to help! :+1:

Best regards
Niklas Wanke

Hi Niklas

Sorry for the delayed response. I just read the message now.

The numbering method was already set in the global settings beforehand.
Is there another menu item that influences this coefficient?

Regards
Natsu

Hi Natsu,

There is no further setting that influences the calculation of the coefficient k_c – apart from the option you have already found in the load-bearing capacity configuration:

“Use factor f to modify X_LT”

The reason that k_c is set to 1.0 in your case is most likely because the existing moment distribution along the member cannot be clearly assigned to one of the cases specified in EN 1993-1-1 Table 6.6. :warning:

The difference between RFEM 6 and RSTAB 8 can arise from a slightly different internal force distribution.

Best regards
Niklas Wanke