Moment magnification factor slender columns ACI 318-19

I would like to report a possible error in RF-CONCRETE Columns in RFEM 5 when designing a slender reinforced concrete column according to ACI 318-19.
I prepared a simple verification model based on the example presented in the Dlubal Knowledge Base article:

Stability of Reinforced Concrete Structures: RFEM vs ETABS” – KB 002069

The model parameters are:

  • rectangular RC column: 1000 × 1000 mm
  • column length: 8.50 m
  • concrete: f'c = 40 MPa
  • reinforcement: approximately 1%
  • axial force: Pu = 10,000 kN
  • bending moment: Mz = 3,000 kNm
  • nonsway column
  • effective length factor in the governing direction: kz = 2.0
  • effective length: kz·L = 17.0 m
  • βdns = 0
  • Cm,z = 1.0

RF-CONCRETE Columns correctly recognizes the column as slender in the z-direction:

λz = 58.89 > λlim,z = 22.0

and calculates:

Pc,z = 46,197.1 kN

However, the program then gives:

δz = 1.0000

and therefore:

Mc,z = 3,000 kNm

i.e. no moment magnification is applied.

Additional inconsistency in the detailed output
There is also a second inconsistency in the detailed calculation output.
For the governing z-direction, RF-CONCRETE reports:
M_(2,z)=3,000 kNm
M_(2,min⁡,z)=452.4 kNm
so clearly:
M_(2,z)>M_(2,min⁡,z)

However, in the detailed output RF-CONCRETE first states:
“Was the minimum moment applied in this direction? – Yes”

while a few lines later it asks:
“Is the design moment M_(2,z)smaller than the minimum required moment according to 6.6.4.5.4?”
and answers:
“No”.

These two statements appear contradictory.
Since:
3000 kNm>452.4kNm

the minimum moment should not govern the design in this direction.

Hello @andre81 and welcome to the Dlubal Community :waving_hand:,

Thank you for the detailed description and the example.

The Knowledge Base article you mentioned is for RFEM 6. However, feel free to send me your RFEM 5 model, and I’ll take a closer look at the calculation and the issues you described.